I used a 14-50 outlet at 40 amps. The s says it’s charging at 29 mi/hr. That should be 8.8 kw. It’s more than enough to charge overnight.We will not know exactly what Telsa will do but I think it's pretty safe to assume that a Gen 3 HPWC will be compatible. The only issue you may have with it is that 150' is a pretty long run that may be long enough to jump you up to a requirement for AWG 4. Ordinariy AWG 6 is adequate. Your electrician will know and will know how to terminate No. 4 properly if it is indeed required.
An HPWC will permit your CT to charge at up to 11.52 kW, it's maximum capacity. Do not install a standard 220V dryer receptacle. The fastest you can charge with that is 5.76 kW which will give you about 11.6 miles added range per hour in a CT (unless, of course, a rate that low is acceptable to you). The HPWC will give you twice that (about 23 miles per hour).